BACnet: Write Node
The BACnet: Write Node allows you to write multiple properties in multiple objects on your BACnet device. This node is only available in Edge Workflows.
There are three main properties that require configuration for this node.
Connection Config
The Connection Configuration contains three fields:
- Host Template: (Required) A string template for the IP address at which the device resides.
- Port Template: (Optional) A string template or integer for the HTTP port. It defaults to port 47808.
- APDU Timeout Template: (Optional) A string template or integer to determine the time in milliseconds until a transaction should be interpreted as an error.
Write Instructions
Write Instructions can be specified in one of two ways, and it is required that one Write Instruction option is configured.
Array of Template Strings
For each Write Instruction, fill out the following input configuration fields, all of which support templating. You must define at least one instruction:
- Object Type: (Required) This field can either be an integer or a template but it must resolve to a valid object type value.
- Object Instance: (Required) This field can either be an integer or a template but it must resolve to a valid instance number. This should resolve to an integer between 0 to 4,194,302 inclusive.
- Object Property ID: (Required) This field can either be an integer or a template but it must resolve to a valid property identifier value.
- Property Index: (Required) A string template or integer for the array index of the property to be written. This should only resolve to an integer greater than 1.
- Write Value Type: (Required) This field can either be an integer or a template but it must resolve to a valid value type (Clause X.3.11).
- Write Value: (Required) A string template or integer for the actual value to be written.
- Write Priority: A string template or an integer to set the priority to be used for writing to the property. This priority will be set against the other objects in the current write property call. This should resolve to an integer between 1 (highest) to 16 (lowest) inclusive. If the priority is not mentioned, it defaults to 16. Read more information on BACnet writing priority.
Payload Path
Enter a payload path that resolves to an array of Write Instructions to be run on this node. The following are the object properties that each object in the array should contain for successful attempts:
- type: (Required) This field can either be an integer or a template but it must resolve to a valid object type value.
- instance: (Required) This field can either be an integer or a template but it must resolve to a valid instance number. This should resolve to an integer between 0 to 4,194,302 inclusive.
- propertyId: (Required) This field can either be an integer or a template but it must resolve to a valid property identifier value.
- propertyIndex: (Required) A string template or integer for the array index of the property to be written. This integer must be greater than 1.
- writeValueTypeTemplate: (Required) This field can either be an integer or a template but it must resolve to a valid value type (Clause X.3.11).
- writeValue: (Required) A string template or integer for the actual value to be written.
- writePriority: A string template or integer to set the priority to be used for writing to the property. This should resolve to an integer between 1 to 16 inclusive. If the priority is not mentioned, it defaults to 16.
The following is an example of an array:
"type": 0,
"instance": 8,
"propertyId": 3,
"key": "bacnetWriteKey1",
"propertyIndex": 395,
"writeValueTypeTemplate": 12,
"writeValue": "Some write value",
"writePriority": 1
The Destination Path (a payload path) is optional, but if you want to confirm that the write was successful, the path should be set. If set, the result of write instruction should be as follows: successful writes will have a value of true
, and failures will have a value of false
If any errors occurred, there will be an errors
key in the object at your path defining the error that occurred.
Node Examples
If all write instructions were successful, the output will be similar to:
"destination": {
"write": true
If an error occurred the output will be similar to:
"destination": {
"bacnetWriteOutput": {
"write": false
References