Modbus: Write Node
The Modbus: Write Node allows you to write to multiple registers on Modbus-enabled PLCs. This node supports Modbus RTU and Modbus TCP. It is only available in Edge Workflows.
There are two main parts of the configuration for this node.
Address Configuration
Address Configuration contains four fields:
- Connection Type: This field can be
TCP Connection
,Serial RTU Connection
orSerial ASCII Connection
. Depending on which type you select, different connection options will be available. For serial connections, here is more information on the difference between RTU and ASCII.
TCP Connection Configuration
- Host Template: (Required) A string template for the IP address at which the register(s) resides.
- Port Template: (Required) A string template or integer for the HTTP port.
Modbus RTU or ASCII Serial Connection Configuration
RTU Serial is only available on Gateway Edge Agent v1.10.0 and higher. ASCII Serial is only available on Gateway Edge Agent v1.46.0 and higher.
- Path Template: (Required) A string template or path that resolves to the serial port at which values will be written.
- Baud Rate Template: (Required) The baud rate, speed of communication over a data channel, which by default is
9600
. This field can either be a integer or a template but it must resolve to a valid rate. For agent versions prior to 1.19.2 the following are the accepted baud rates:110
,300
,600
,1200
,2400
,4800
,9600
,14400
,19200
,38400
,57600
,115200
,128000
,256000
. As of GEA v1.19.2 you may specify any positive integer for this field.
In GEA v1.10.0 the following options are defaulted:
- Data Bits:
8
- Stop Bits:
1
- Parity:
none
However, in GEA v1.11.0 and higher, you may specify these options.
- Parity Template: The Parity is a method used to detect errors, which by default is
none
. This field can either be a string or a template but it must resolve to one of the following valid options:none
,even
,mark
,odd
,space
. - Data Bits Template: The Data Bits is the number of bits each character can be, which by default is
8
. This field can either be a integer or a template but it must resolve to one of the following valid data bits:5
,6
,7
,8
. - Stop Bits Template: The Stop Bits is the bit sent at the end of ever character to signify the end of a character, by default this is
1
. This field can either be a integer or a template but it must resolve to a valid stop bit. The only valid stop bits are1
and2
ASCII Serial Connection has one additional option.
- Start of Frame Character Template: The ASCII character that is the starting bit of the frame. This field defaults to
Common Configuration
- Unit ID: (Required) A string template or integer for the Unit ID at the specified host and port. Defaults to
1
. - Timeout Template: A string template or integer for the numbers of milliseconds to wait before a timeout will occur while waiting for write results. Defaults to 30000 milliseconds.
Write Instructions
Write Instructions can be given in two ways, either is required.
Array of Template Strings
For each write instruction, fill out the following input configuration fields; all of which can utilize templates. You must define at least one instruction.
- Address: (Required) A string template or integer for the address at which to write. This should resolve to an integer between
0
and65535
inclusive. - Register Type: (Required) -
Holding Register
: (default) Present single register (FC=06) -Coils
: Present single coil (FC=05) -Holding Registers
: Present multiple registers (FC=16) - Value: (Required) A string template or integer or path, depending on the register type, to specify the value to write to the address. If the register type is
Holding Register
then this should resolve to an integer between0
and65535
otherwise if the type isCoils
the value should be a single bit. If the register type isHolding Registers
then this value expects a path to an array on your payload of integer values to write to the registers. - Result Key: (Optional) A key on the destination path to note the result of this write instruction. If a key is not specified, it will default to
addr-${Number(address)}
. Data will only be available if the destination path is also set. The value at this key will always be a boolean,true
for success, andfalse
for failure. Note If you are reading from the same address on different types, it's possible to overwrite one of your keys, which could result in unexpected behavior.
Payload Path
Give a payload path that will resolve to an array of write instructions to be run on this node. The following are the object properties that each object in the array should contain for successful attempts:
- type: (Required) one of the following types:
holding-register
,holding-registers
, orcoil
. - address: (Required) An integer or array of integers for the address at which to write. This integer(s) must be between
0
and65535
. - value: (Required) An integer value to write to the specified address.
- key: (Optional) The key on the destination path to note the result of this write instruction. This data will only be available if destination path is also set. The value at this key will always be a boolean,
true
for failure. If the key is missing, it will default toaddr-${Number(address)}
"type": "coil",
"address": 3,
"value": 0,
"key": "coil-3"
"type": "holding-register",
"address": 3,
"value": 0,
"key": "hReg-3"
"address": 1,
"value": 3
"type": "holding-registers",
"address": 5,
"value": [1, 2, 3, 4, 5]
Note: This option is only available in GEA version 1.9.0 and higher.
Destination Path
The Destination Path (a payload path) is optional, but if you want to confirm that the write was successful, the path should be set. If set, the result of write instruction will be at a key in the format of addr-${Number(address)}
, successful writes will have a value of true
, and failures will have a value of false
If any errors occurred, there will be an errors
key in the object at your path defining each error that occurred. The only time you will get a single error for multiple writes is if the connection could never be made to the Modbus itself.
Node Examples
For example, say we want to write to two addresses (one at 23
, and the other at 80
), where address 80 has a key of foo
, and we set our Destination Path to destination.output
. If all write instructions were successful, the output will look like the following:
"destination": {
"output": {
"addr-23": true,
"foo": true
If an error occurred the output will look like the following:
"destination": {
"output": {
"errors": [
{ "type": "MODBUS_WRITE_ERROR", "message": "Some error occurred at 23" },
{ "type": "MODBUS_WRITE_ERROR", "message": "Some error occurred at 80" },
"addr-23": false,
"foo": false
If an error occurred for one write instruction, that does not mean all writes were unsuccessful. If one is successful and the other is not the output might look like the following:
"destination": {
"output": {
"errors": [
"addr-23": false,
"addr-80": true